How Can ACI 318-19 Provisions be used for Extension Design of Post-Installed Reinforcing Bar?
Post-installed reinforcing bars evaluated per AC308 Table 3.8 can be designed using the ACI 318-19 development and lap splice provisions applicable to cast-in reinforcing bars. Development length (ℓd) and tension lap splice length (ℓst) are calculated using Chapter 25 requirements.
The American Concrete Institute (ACI) standard titled Building Code Requirements for Structural Concrete (ACI 318) includes provisions for reinforced concrete design. These provisions are written for cast-in reinforcing bar design; however, post-installed reinforcing bars that demonstrate equivalency to cast-in bars can also be designed for development with these provisions. This paper will discuss how the development and splice provisions given in ACI 318-19 Chapter 25 can be used to design post-installed reinforcing bars for a tension lap splice.
Term | Definition |
Development Length (ℓd) | Embedment length required to develop the full yield strength of reinforcement |
Tension Lap Splice Length (ℓ st) | Length required to transfer tension from one reinforcing bar to another |
AC308 | ICC-ES acceptance criteria used to qualify adhesive anchor systems for post-installed reinforcing bars |
ESR | ICC-ES Evaluation Report containing product-specific design requirements |
Confinement Term ((cb + Ktr)/db) | Parameter used to account for concrete cover and transverse reinforcement |
hef | Effective embedment depth of the post-installed reinforcing bar |
db | Reinforcing bar diameter |
d0 | Drilled hole diameter |
The International Code Council Evaluation Service (ICC-ES) writes what are known as “acceptance criteria” to permit the evaluation of products for recognition “in the opinion of ICC-ES” under the International Building Code (IBC). IBC recognition is provided via an ICC-ES evaluation report, also known as an “ESR.” The ICC-ES acceptance criteria for evaluation of adhesive anchor systems under the IBC is titled Acceptance Criteria for Post-Installed Adhesive Anchors in Concrete Elements (AC308). Evaluation per AC308 also provides product-specific data and provisions that can be used to design the adhesive anchor system with ACI 318 provisions. Reinforcing bars successfully evaluated per the test program outlined in AC308 Table 3.8 can be post-installed as part of an adhesive anchor system in which the bars are designed using ACI 318 development and splice provisions (e.g., ACI 318-19 Chapter 25 provisions).
Below is an excerpt from ESR-3814 (HIT-RE 500 V3 adhesive) showing the cover and spacing requirements for post-installed reinforcing bars being designed for development. The test programs outlined in Table 3.8 of AC308 are predicated on bar embedments greater than 20-bar diameters (20db in). ACI 318 cover requirements are predicated on the amount of concrete between the outside of a bar and the concrete surface, and spacing requirements are predicated on the clear spacing between bars. It is important to note that cover requirements derived from the AC308 evaluation are predicated on the distance from the center of the post-installed bar to the concrete surface, and spacing requirements derived from the AC308 evaluation are predicated on the center-to-center spacing between bars. The parameter “d0” noted below corresponds to the drilled hole diameter (d0 in) for the post-installed reinforcing bar, which is different than the bar diameter (db in). Values for d0 are given in the ESR. Also, note that the spacing requirements between two post-installed bars differ from the spacing requirements between a post-installed bar and an existing cast-in-place bar.
ACI 318-19 Section 25.4 contains provisions for developing cast-in reinforcing bars. These provisions will be explained below, keeping in mind that post-installed reinforcing bars qualified per the test program outlined in AC308 can also be designed with these provisions. Any exceptions to these provisions with respect to post-installed bar design versus cast-in design will be noted. In the context of this paper, the discussion emphasis will be on those sections in Section 25.4 that are relevant to straight bar tension reinforcement designed for development.
ACI 318-19 Section 25.4.3 includes provisions for designing a hook. Using a hook for reinforcement design permits a bar to be developed when there is insufficient concrete to develop a straight bar. Figure 1 shows the red bars' calculated straight bar tension development length (ld in). This length is greater than the grade beam thickness of 36 in. Therefore, a 900 hook can be used to develop the bars in tension. Figure 2 shows the hook length (ldh in) calculated per the provisions given in Section 25.4.3.1 and the parameters defined in Table 25.3.1. When designing a post-installed reinforcing bar for development, only a straight bar can be installed in the hole that must be drilled into the existing concrete. Therefore, post-installed reinforcing bars cannot be designed with a hook at the end that is installed into existing concrete. However, a hook could be designed for the end around which new concrete will be placed.
ACI 318-19 Tension Lap Splice Provisions for Reinforcing Bars
ACI 318 includes provisions for splicing one bar to another to transfer load from one concrete member to another. Provisions for both tension lap splices (bars in tension are spliced to one another) and compression lap splices (bars in compression are spliced to one another) are included. This paper will discuss ACI 318-19 tension lap splice provisions.
Adhesive anchor systems successfully evaluated per the test program outlined in Table 3.8 of the ICC-ES acceptance criteria AC308 demonstrate compliance with the IBC and performance equivalent to cast-in reinforcing bars. This is done so that the post-installed bars can be designed using ACI 318 development and splice provisions. The ICC-ES evaluation report (ESR) for Hilti adhesive systems will note if the adhesive product has been evaluated per AC308 Table 3.8. Reference Section 6.0 in the ESR. Section 4.2 in the ESR will state that the adhesive can be used to post-install reinforcing bars per the development and splice provisions of ACI 318. The attached example shows how post-installed reinforcing bars can be designed with a Hilti adhesive product per the development and splice provisions in ACI 318-19.
Quick Reference Guide
Parameter | Source |
Development Length (ℓd) | ACI 318-19 Section 25.4 |
Lap Splice Length (ℓst) | ACI 318-19 Section 25.5 |
Minimum Cover | ACI 318-19 Section 20.5.1.3 |
Reinforcement Spacing | ACI 318-19 Section 25.2 |
Qualification Method | AC308 Table 3.8 |
FAQ
What is the difference between a Class A and Class B splice?
Please refer to ACI 318-19 Table 25.5.2.1 to determine if you need to use Class A or Class B.
Table 25.5.2.1 – Lap splice lengths of deformed bars and deformed wires in tension
As,provided / As,required [1] over length of splice | Maximum percent of As spliced within required lap length | Splice type | ℓst |
≥ 2.0 | 50 | Class A | Greater of: 1.0ℓd and 12 in. |
≥ 2.0 | 100 | Class B | Greater of: 1.3ℓd and 12 in. |
< 2.0 | All cases | Class B | Greater of: 1.3ℓd and 12 in. |
[1] Ratio of area of reinforcement provided to area of reinforcement required by analysis at splice location.
Question 2: Why does Profis Engineering Concrete to Concrete Module give me a different development length output when I change the diameter of the existing cast in bar?
Based on ACI 318-19 Section 25.5 If bars of different size are lap spliced in tension, ℓst shall be the greater of ℓd of the larger bar and ℓst of the smaller bar.
You can learn more about Post-Installed Reinforcing Bar design by referencing the following:
Additional Resources
Design Guides
Hilti Post-installed Reinforcing Bar Design Guide
Hilti Post-installed Reinforcing in Fire Conditions Design Guide
Design Software
Hilti Post-Installed Rebar White Papers
Shear Friction Design using the Hilti Method for Post-installed Rebar Design
Design for Yield using Anchoring-to-Concrete Provisions for Post-installed Reinforcing Bar Design
Extension Design using ACI 318-19 Provisions for Post-installed Reinforcing Bar
Shear Friction using ACI 318-19 Provisions for Post-installed Reinforcing Bar Design